Ampere Difference between Drives

Posted in: , on 2. Apr. 2011 - 17:04

Dear Experts,

Please assume that there are two VVVF ( Variable Voltage and Variable Frequency ) drives are installed in a single conveyor having specification of ST1000. What should be the maximum ampere differences can be allowed between the two motors? Because, more the difference will affect the belt & it's joints.

Thank you all & Regards,

Lyle Brown
(not verified)

Re: Ampere Difference Between Drives

Posted on 3. Apr. 2011 - 01:15
Quote Originally Posted by sganeshView Post
Because, more the difference will affect the belt & it's joints.

Not an expert, though:

Are you able to qualify the above statement?

Regardless, what load sharing was the conveyor designed for?

Given you have VSD why can't you achieve "equal" load sharing?

Regards,

Lyle

Re: Ampere Difference Between Drives

Posted on 3. Apr. 2011 - 02:26

Dear Mr.Lyle Brown,

If there are amperes differences between the motors of individual drive pulleys, I think their RPMs would also vary. This may cause frequent slack & tight effect on the belt which is not good for the belt & joints.

I understood from my electrical engineers that slave drive would be always slightly higher load sharing than that of master drive.

I feel that the belt rating would be closely considered in the load sharing.

Thanks & Regards,

Lyle Brown
(not verified)

Re: Ampere Difference Between Drives

Posted on 3. Apr. 2011 - 02:57
Quote Originally Posted by sganeshView Post


If there are amperes differences between the motors of individual drive pulleys, I think their RPMs would also vary.

Fair enough, though could this be corrected via the VSDs?

Given your layout, motor speed is not the only factor (belt stetch, effective diameters etc).

Are you able to review torque load sharing?


Quote Originally Posted by sganeshView Post


This may cause frequent slack & tight effect on the belt which is not good for the belt & joints.

I feel that the belt rating would be closely considered in the load sharing.

Lagging wear maybe as issue?


Quote Originally Posted by sganeshView Post


I understood from my electrical engineers that slave drive would be always slightly higher load sharing than that of master drive.

How large is slight?

Given this is engineering and not science a small margin could potentially be fine, though only the designer could say for sure.

Again could this be corrected via the VSDs?

Regards,

Lyle

Re: Ampere Difference Between Drives

Posted on 4. Apr. 2011 - 03:11

It is normal to have some difference in the amperage however you need to explain, are both motors couple to the same pulley or are they on a twin drive arrangement. If it is a twin drive there is a much bigger issue as you must set the drives up to load share in a manner that does not see any "hunting" between the drives. We need much more detail of what your problem is to really make any comments

Cheers

Col Benjamin

Gulf Conveyor Systems P/L

www.conveyorsystemstechnology.com

Re: Ampere Difference Between Drives

Posted on 4. Apr. 2011 - 04:11
Quote Originally Posted by sganeshView Post
Dear Experts,

Please assume that there are two VVVF ( Variable Voltage and Variable Frequency ) drives are installed in a single conveyor having specification of ST1000. What should be the maximum ampere differences can be allowed between the two motors? Because, more the difference will affect the belt & it's joints.

Thank you all & Regards,

There is elasticity in the belt, however should you be monitoring something other than motor amps to ensure that the two drives are synchronised? Is not the drive speed more important than the motor amps? After all, you are always going to get difference in motor amps because you have mechanical components that are NEVER going to be equal. No matter how "identical" you might want the drives to be, you have clearances and alignment tolerances that will see difference in the internal load on the drives and therefore motor amps. These differences will change throughout the life of the drives.

Just recently the contract I am working on had a fan with one bearing running at around 50 deg C with the other bearing running at over 100 deg C. No matter what the fan supplier did, one bearing would run art more than double the temperature of the the other. In the end, the fan supplier agreed to replace the bearings if they failed, and so far, after some 6 months of fairly heavy use, there has been no issue with the bearings.

[I]Ian A. White, MIEAust. CPEng. RPEQ WAI Engineering [URL="http://www.wai.com.au"]www.wai.com.au[/URL][/I]

Re: Ampere Difference Between Drives

Posted on 19. Apr. 2011 - 03:40

To answer your question, there should be very little difference between the amps drawn between the drives... however..

The trouble is that in practice it depends on a number of things:

- The skill of the chap that sets it up

- Which system you buy, and..

- Does it have a tail drive a long way away??

I have a 7km conveyor with VSD c/w tail drive, and to this day the VSD supplier cannot balance the load sharing, ESPECIALLY DURING START UP.

For conveyors with head drive only, load sharing is relatively simple and to be within 5% is quite achieveable.

Cheers

LSL Tekpro

Graham Spriggs

Re: Ampere Difference Between Drives

Posted on 19. Apr. 2011 - 11:42

Graham,

We have many head and tail drives working with high satisfaction. The drives cannot load share during starting, unless you have a very rigid or frigid belt. But, I believe this would be evident with your dynamic analysis program. (Written by you?).

Our head and tail drives load share within 1-2% of demand summary. We write our our control codes. Works for fluid couplings, wound rotor drives, and VFD when in velocity control and load sharing algorithm.

Howver, there are conveyors that must be designed with tail drive that does not load share. This is the nature of what and why the designer wishes to do and knows how to do it.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Re: Ampere Difference Between Drives

Posted on 19. Apr. 2011 - 11:55

Slight clarification:

The drives can be made to load share during steady-state running, but, not during starting and stopping. Think elastic belt and elastic waves.

They can be made to load share during starting and stopping at great increase in start-stop timing.

Control algorithms come in many varieties, which are the IP of the experts. Usually, there is an Objective Function such as:

1. controlled belt stress with respect to belt rating

2. minimum starting torque together with minimum belt stress - motor is capped separate from belt tension limit.

3. horizontal curve transverse motion control

4. incline and decling product stability

5. motor torque limit

6. brake regulation and control schemes

7. drive slip

8. take-up stability and regulation of oscillation

There are many other control algorithms, but, the discussion becomes more complex and off track.

Hire an expert to solve your problems. Problem is - who is an expert? Ask and you will find many with raised hands. Hopefully, this forum gives some clues.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Re: Ampere Difference Between Drives

Posted on 20. Apr. 2011 - 12:09

WAI Engineering:

Dual or more drive pulley speeds, located in near proximitiy, cannot synchronize without serious problems. Since the belt length contracts across a positively powered drive pulley (T1 into T2), a following secondary drive will always run slower than the primary, given the local belt speed is judged by the belt speed entering "the" drive pulley. Reality is a little different, but the concept is the same.

You may wish to load share on amps or regulate on volts (torque) with most VFD's. Most VFD's (Variable Frequency Drives) applied to conveyors use voltage (torque) and frequency (speed) for regulation. In fact the regulator is: Volts/Hz. Current regulation can be used, but, is typically a different type of inverter: VFVV (Very-Frequency-Very-Voltage) drive vs. VC (Very-Current) drive.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Re: Ampere Difference Between Drives

Posted on 20. Apr. 2011 - 12:24

SGANESH:

To you original question: What is an allowable difference in amperage, with dual drives on dual pulleys for a ST-1000 N/mm rated belt? Like all things in life, more needs to be known such as the belt width, belt speed, drive efficiencies, .......

In simple terms, assuming the amps = tension, then a 10% variation is acceptable, a 20% is probably not if you must then factor in: starting, stopping, dead-band regulation, slew rate latency, age of belt, prior history of abuse (cruelty), irregularity of pulley geometries, proximity to idler transition distance, proximity to dirty side pulleys and badly loacated snubs, belt tracking error anticipated or observed, perfection of splice construction, belt safety factor, ....... shucks, and a whole lot more.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Re: Ampere Difference Between Drives

Posted on 20. Apr. 2011 - 03:01

Thank you very much Mr.Nordell and others.

High regards to all,

Re: Ampere Difference Between Drives

Posted on 3. May. 2011 - 05:14

Larry

I have had no problem load sharing between head and tail drives during on anything other than variable frequency, variable speed drives.

Even up to 12.8km long horizontally curved conveyor, using good old Scoop Control couplings.. no problem.

Even 4km using TSS traction couplings on the head drives and tail drives .. no problem as long as the drives and pulleys are identical and the sequencing is correct.

But the VSD boffins don't seem to get the hang of it during starting for some reason.

I hope they crack it before we commission the 21km overland conveyor system I am currently designing.

(And indeed, my dynamic analysis programme was written by your favourite old South African conveyor designer with the white hair, at some time, during his sheltered existence.)

Cheers

LSL Tekpro

Graham Spriggs

Amperes To Rpm Graph

Posted on 5. May. 2011 - 06:38

Dear all,

Our electrical engineers created to get graph on RPM of individual motors, installed approx 100 meters apart. Now we are analysing the RPM difference , which can make the pulling or slipping of the belt which is not advisible. But I do not know how much difference can be allowed for pulling?

Belt is ST 1000 which is going under pulling stress and both drive pulley diameters are 810 mm.

Thanks & regards,

Re: Ampere Difference Between Drives

Posted on 5. May. 2011 - 03:45
Quote Originally Posted by sganeshView Post
Dear all,

Our electrical engineers created to get graph on RPM of individual motors, installed approx 100 meters apart. Now we are analysing the RPM difference , which can make the pulling or slipping of the belt which is not advisible. But I do not know how much difference can be allowed for pulling?

Belt is ST 1000 which is going under pulling stress and both drive pulley diameters are 810 mm.

Thanks & regards,

Sorry Sganesh..

...but I don't understand what you are trying to say.

LSL Tekpro

Graham Spriggs

Re: Ampere Difference Between Drives

Posted on 5. May. 2011 - 03:53

Dear Mr.Spriggs,

I feel that comparing the individual motors RPM is more appropriate than considering the amperes.

The differences of RPMs of motors may create unwanted stress between the drive pulleys.

I am wondering how much maximum difference of RPMs can be allowed. Both the gearboxes are having same ratio.

Thanks & regards,

Re: Ampere Difference Between Drives

Posted on 6. May. 2011 - 02:23

Hi Sganesh

Not really better to measure the pulley rpm, as the outside diameters of the pulleys are never identical, and I have often come across supposedly identical gearboxes, but have found that their exact ratios sometimes actually differ.

The Amps measured however, relates directly to the load on each drive, and so you can directly check the load sharing.

I normally ask for a print out from the control room, of a 24 hour trace for the Amps. This enables me to immediately see the accuracy of the load sharing during starting as well as running for the various loading conditions during the day. I can then make the necessary adjustments as required.

Good luck

Graham Spriggs

Re: Ampere Difference Between Drives

Posted on 7. May. 2011 - 07:14

Thanks a lot Mr.Spriggs.

I am trying to compare the motor rpm. The differences of pulley diametres and gear box ratio should be always constant. But I find the motor RPMs are fluctuating. What should the reason ? I worry because this can affect the joints.

Regards,

Re: Ampere Difference Between Drives

Posted on 7. May. 2011 - 07:15

Thanks a lot Mr.Spriggs.

I am trying to compare the motor rpm.

The differences of pulley diametres and gear box ratio should be always constant.

But I find the motor RPMs are fluctuating. What causes them? I worry because this can affect the joints.

Regards,

Re: Ampere Difference Between Drives

Posted on 7. May. 2011 - 06:17

Dear Mr.Spriggs,

I have asked to monitor the motor RPMs which are fluctuating. ( Not pulley RPMs ).

What could be the reason for fluctuating of motor RPMs?

Regards,

Re: Ampere Difference Between Drives

Posted on 7. May. 2011 - 09:15

Dear sganesh,

Low frequency resonance?

Have a nice day

Teus

Teus

Lyle Brown
(not verified)

Re: Ampere Difference Between Drives

Posted on 8. May. 2011 - 12:46

1. It is unlikely that the motor speeds should be the same (given the belt relaxing / change in length and hece required speed etc).

2. How confident are you that the motor speed relates well with pulley speed (i.e. pulley diameters etc)?

3. It is not unheard of for VSD's drives to "hunt". Consider reviewing the set up of your VSD's.

4. Not that it matters, though we are yet to be convineced you had a problem originally.

Regards,

Lyle

Re: Ampere Difference Between Drives

Posted on 11. May. 2011 - 07:10

Dear all experts,

1. By comparing the amperes of the drives in the graph, I can understand the reason for "hunting" during initial period of starting the conveyor for few seconds, due to the up & down movements of vertical gravity take up, which may affect the motor RPMs also.

2. Motor speed affects the pulley speed, which causes the looseness or tightness of the belt. Or my understanding of this question is not correct.

3. First drive is installed at least one kilometer away from the tail end vibrofeeders.

( Master drive ). The Slave drive 1 is still 70 meters away from the master drive.

When the vibrofeeders are started, "hunting" not takes place.

But when vibrofeeders are stopped, "hunting" takes place.
I do not know why it is happening.

4. One joint was snapped on 28.03.2011. Another joint was also found badly damaged on the same day. I feel "hunting" was the reason for the joint damages, if it goes beyond certain value. I remember, Mr.Nordell's advice that maximum 10% of amperes difference is acceptable.

Now we are measuring the motor RPMs and made a logic such that if the RPM difference goes beyond 27, conveyor will be tripped. The above figure was based on the monitoring of motor RPMS. I do not have any design reason for this.

The distance between the drives is 70 meters. Pulley diameters are 800 mm. Gear Box ratio is 18:1. Based on the above the belt in between the drives may be tightened for 67 mm approximately. Belt being used is ST 1000. Belt width is 1400 mm. Request your opinion on this.

There is another drive ( Slave drive 2 )at the extreme tail end nearer to the vibrofeeders. Its ampere is same though its gearbox is coupled with conveyor or not. But if it is taken in line, the synchronization of the Master & slave drive 1 is smooth.

I do not understand the comment " Low Frequency Resonance " by Mr.Teus Tuinenburg.

Regards & Thanks to all for your active contribution.

Re: Ampere Difference Between Drives

Posted on 11. May. 2011 - 03:10

Dear sganesh,

I assume that a belt conveyor with drums, drives and load, together with a flexible belt forms a mass-spring system that has its own resonance frequency.

In case there is a master and slave control, set with a too high magnification (strong reaction on small disturbances), another resonance can occur (hunting)

If the 2 resonance frequencies coincide, you have a real problem.

May be a case for a DEM calculation?

Have a nice day

Teus

Teus

Re: Ampere Difference Between Drives

Posted on 6. Jul. 2011 - 06:51

Thanks a lot Mr.Teus & other Experts!

How the Master, Slave 1 & Slave 2 drives are selected in the conveyor, which has individual drive units at different places ? I feel that they are based on the belt tension.

i.e, the drive pulley which go under maximum load is Master, the second highest tensioned drive pulley is Slave 1 and so on. Please correct me if I am wrong.

Before few days we took trial.

Trial A : When we increase the counter weight, the RPM differences of Master & Slave 1 goes high. I am nervous , because this may cause pull-push effect between the drive pulleys, which may affect the joints.

Trial B : When we made all the motors RPM uniform by adjusting the parameters, only master drive is taking maximum ampere.

Both above trials are at idle running. ( Zero feeding to the conveyor ).

What is your advice ? Have you ever faced similar problem ? Is it mechanical or electrical ?

We could not achieve the designed capacity of the conveyor.

I will be thankful, if I am getting some light by your answers.

Thanks to all & Regards,

Re: Ampere Difference Between Drives

Posted on 6. Jul. 2011 - 08:46

Dear sganesh,

What you did in your test was tuning a 3 mass/spring system.

The system is buildup from the moment of inertia of the master drive – the inertia of the counter weight – the moment of inertia of the slave drive.

By increasing the counterweight’s mass, the resonance increased, proving that, under those conditions, the system was running close to the resonance frequency.

By setting the drive rpm’s equal, with the result that the drive motor took the complete load, you virtually uncoupled the slave drive. (actually virtually decreasing its moment of inertia to zero)

Here, it is proven that the setting of the VSD’s are also influencing the system.

As you did the trials under no belt load (idle running), the situation can (will) be totally different under situations where the belt is loaded with material.

Undoubtedly a mass-stiffness resonance problem.

Your only option is to call in an expert (Lawrence Nordell Conveyor Dynamics, Inc.) in resonance dynamics and let him calculate the critical frequencies under all conditions.

From these calculations it must be possible to extract a solution.

Success

Teus

Teus

Rpm Deviation Between Drives

Posted on 7. Jul. 2011 - 03:37

Could you please specify what you mean by fluctuations?

Frequency, amplitude; FFT pattern?

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Drive Rpm Fluctuations

Posted on 7. Jul. 2011 - 03:49

I Thinrk I have said this before:

Pulley lagging or diamter irregularity of 1% can result in a 100% drive fluctuation with a 1% slip efficient motor.

Same can be said for near proximity snub pulleys as they tug and loosen the belt strand captured between drive and drive or drive and snubs. These conditions are made worse by material build up or when material falls into the interface between belt and pulley.

VFD drives are complex devices that need to be detuned for belt conveyors to allow for small (< 0.1% dimensional repeated changes in the pulley diameter. Diameter changes are measured from the belt's neutral tensile axis. Thus, belt anomalies can contribute to aberrations in drive flux.

You can improve the local aberrations by adjusting the slewing rate of current and/or voltage changes that are allowed in the load regulating algorithm within the VFD. Talk to your provider. VFD's are usually adjusted to change at a faster rate than necessary or desirable for conveyor applications.

Get an expert to assess your problem. Fish for carp means you like carp.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450